Maximum Permissible Speed
Started by ahmedensem, Feb 02 2012 03:31 AM
7 replies to this topic
Share this topic:
#1
Posted 02 February 2012 - 03:31 AM
hello everyone,
I'm traying to size my pipe transferring Fuel for a project in morocco.So to determine the diamter's pipe I need know the permissible speed of the Fuel in this pipe,which make necessary for me asking if there is a standard fixing this speed between two values?
any help will be very appreciate
Regards
I'm traying to size my pipe transferring Fuel for a project in morocco.So to determine the diamter's pipe I need know the permissible speed of the Fuel in this pipe,which make necessary for me asking if there is a standard fixing this speed between two values?
any help will be very appreciate
Regards
#2
Posted 02 February 2012 - 03:47 AM
let you use the search button , key words : pipe maximum velocity .
It should help
Breizh
It should help
Breizh
Edited by breizh, 02 February 2012 - 05:47 AM.
#3
Posted 02 February 2012 - 04:05 AM
As a rule of thumb process engineers consider the following maximum velocities:
For Liquid Line Max 15 ft/sec
For Gas Lines Max 60 ft/sec
For Liquid Line Max 15 ft/sec
For Gas Lines Max 60 ft/sec
#4
Posted 03 February 2012 - 03:50 AM
thinks friends,I got it
#5
Posted 03 February 2012 - 08:30 AM
I believe Zak is quoting wrong velocities. The nominal design velocities employed in process design of piping I have always worked with are:
For Liquid Lines: (Normal) 5 ft/sec; Max. = 10 ft/sec
For Gas Lines: (Max) 100 ft/sec
For Liquid Lines: (Normal) 5 ft/sec; Max. = 10 ft/sec
For Gas Lines: (Max) 100 ft/sec
#6
Posted 03 February 2012 - 02:06 PM
You can find line sizing criteria in http://www.cheresour...id-line-sizing/ '> http://www.cheresour...id-line-sizing/ , posts of 6 Oct 2011. Data seems to generally comply with post No 5, with more details reported.
#7
Posted 06 February 2012 - 01:46 AM
ZAK's sizing criteria is highly acceptable as it is based on API RP-14E.
We can alter the design criteria depending on which code or standared we are following.
We can alter the design criteria depending on which code or standared we are following.
#8
Posted 06 February 2012 - 08:04 AM
The Criteria I mentioned are based on "Recommended Practice for Design and Installation of Offshore Production Platform Piping Systems API RECOMMENDED PRACTICE 14E (RP 14E)"
Similar Topics
Short Path Distillation Rotor SpeedStarted by Guest_MEC_* , 11 May 2023 |
|
|
||
Transfer Water By Gravity - Maximum Velocity CriteriaStarted by Guest_56200358_* , 05 Mar 2025 |
|
|
||
Maximum Allowable Accumulated PressureStarted by Guest_mahmooddalvi09_* , 30 Jan 2025 |
|
|
||
Maximum Mass Flow In A Shell & Tube Heat ExchangerStarted by Guest_DonStalke_* , 22 Sep 2024 |
|
|
||
Maximum Velocity For Piping In Fire Water Distribution System (Fire WaStarted by Guest_applepe_* , 06 Sep 2024 |
|
|

FB